Designing a panel that will control some motors and customer told me the FLA for the 1/2hp blower motor is 2A (@480V/3ph). This sounded at least 2x too high, so asked for a picture of the nameplate. Attached.
I agree that this is what it looks like it shows (0.5HP and 2A for 460V). Isn't this current wildly high for 1/2hp?
I can't get to that same current even after considering the efficiency and awful PF listed. I don't think I've seen a nameplate FLA so much higher than NEC FLC table.
(There's something like 12 of them that we are controlling and supplying, so any error is off by 12x).