3/4 " SLB volume for wiring.

steve61

licensed Electrical Contractor
Location
Nebraska
Occupation
Electrician
I am installing a 3/4 " SLB with 3 # 6 thhn wires and one # 10 thhn EGC. The inside of the SLB is marked " 3 # 6's Maximum" . Does this mean that I have to install a larger SLB to make room for the # 10 ground wire, Or am I allowed to run the ground wire without exceeding the max fill of the SLB ?
 
If this were a standard LB conduit body then with #6 conductors the fill would be the same as that of the attached raceway. Since it's an SLB I don't believe that you're permitted to exceed the listed conductors on the SLB which would limit you to 3-#6 conductors. Any reason why you're using an SLB over a standard LB?
 
It appears to be a standard LB and that is what is stamped on the outside of the body. I needed three of the same kind so I took three of the same kind off of my parts shelf so they would all look the same. I later found two others also marked LB , but they do not have the same info inside. Inside they are marked " Max wire size # 6 AWG ". On the outside they are marked " 7.3 CU. IN. volume ".
 
Inside they are marked " Max wire size # 6 AWG ".
That makes sense because #4 AWG and larger must comply with the 6X rule. #6 and smaller do not have to comply with the 6X rule so the limit is the raceway fill attached to the conduit body.
 
Are they oversized as compared to a regular LB?
I see they have an offset. I'm guessing this is for coming out the top of the meter, or disconnect?
It's different in that the "hub" surface (where the threaded portion that would normally go through the wall) is flush with the back of the LB. For a normal LB the "hub" part (for lack of a better word has to go into the wall.
 
It's different in that the "hub" surface (where the threaded portion that would normally go through the wall) is flush with the back of the LB. For a normal LB the "hub" part (for lack of a better word has to go into the wall.
Took a minute, but I finally pictured what you were saying. It would have been easier if the image was flipped up 90 deg.
 
I am connecting the three LB's to a junction box with chase nipples. This is a 480 VAC circuit with a bonding bushing at the feed disconnect. Can I use chase nipples, or do I have to use a regular nipple with a bonding bushing in the junction box ?
 
I am connecting the three LB's to a junction box with chase nipples. This is a 480 VAC circuit with a bonding bushing at the feed disconnect. Can I use chase nipples, or do I have to use a regular nipple with a bonding bushing in the junction box ?
If there are concentric or eccentric KO'S you cannot use the chase nipples because you'll need a bonding bushing. There is also the question if using a chase nipple with a conduit body (done all of the time) is even code compliant. I always use a close nipple even when I'm not using a bonding bushing.
 