I’m being told by an inspector the following.
(1)- An emergency disconnect is required on a pole barn ( non dwelling unit 200’ from the house) that’s located on a residential property and supplied from the POCO with its own meter .
(2)- AN exterior disconnect is required on the pole barn mentioned above. Just a disconnect.
I’m disputing (1) because it’s not a dwelling unit.
I’m disputing (2) because it has a main breaker panel immediately inside the structure.
An I incorrect on one or both of these.
Thanks