It sets it to 120V as default, I can make it any number. But my suspicion is that it's supposed to be L-G because that's the worst case since L-G fault gives you a much higher voltage drop for the ECGIn your GEMI screen shot under system parameters > Operating voltage you set 120 volts? I would think that should be your L-L voltage for voltage drop on a feeder?
at 2x or 3x the breaker would still trip though. Code doesn't specifically say how fast the breaker is supposed to trip though... at 3x for example a Siemens 200A HQS breaker would trip between 15-90 seconds. Is this even good enough?This is about the voltage drop and the fault clearing properties of the EGC...it uses the line to ground voltage and not the line to line voltage. However using 5x the OCPD rating for the ground fault current seems very low. I would expect for many systems using 3/0 the available line to ground fault current would far exceed 625 amps.