Can 220.83 (a) be used to calculate the optional standby system (generator) size for a whole house automatic transfer as per 702.4 (b)(2)(a) on a dwelling unit?
Where in 220.82 does it say the load has to be at least 24kVA?Thats my go to these days, 220.82 requires the load to be at least 24kVA, no such limit in 220.83(A) in my 2023 book.
I believe he is citing the part where it allows you to use that section if it is 100amps or more. 24kw/240 = 24000/240= 100Where in 220.82 does it say the load has to be at least 24kVA?
Oh, got it.I believe he is citing the part where it allows you to use that section if it is 100amps or more. 24kw/240 = 24000/240= 100