Mfg. label on A/C condenser says MCA 28.3 with 50a max breaker. So #10Cu to a 50a ocpd. Simple enough. Done. But the Homeline 50a 2pole has printing on the case that only describes #8 (or #6 ~ #2). Is this a lug restriction for all use scenarios?
I can run 4ft of #8 from breaker to the existing junction box & splice to the remainder of the run that uses #10 but I’m curious if I have an out here?