Thanks Jim…important point to remember, if I can.Yes. Even fused switches are tested with conductors so a 20A 100kAIC current limiting fuse would also protect #12 conductors.
Thanks Jim…important point to remember, if I can.Yes. Even fused switches are tested with conductors so a 20A 100kAIC current limiting fuse would also protect #12 conductors.
To add a little to this, if you have 100kA available how often do you have (or desire to have) 15 and 20 amp circuits connected to the equipment that has that much available? Often that is main distribution type equipment and only supplies feeders or if there is branch circuits they are some large capacity load. Usually your general use branch circuits are on some some feeder or even have a transformer in the path and the fault current at the origin of those branch circuits is likely below 10kA or at least has series rated components involved. At very least a 22-25 kA main breaker in that branch panel that is series rated for use with the 10kA branch breakers, which that combination will be covered even by most commonly used "load centers" you find in residential installs.However, you will have to find some way to limit the fault current on the line side of the 20 amp breaker that feeds these loads. Unlikely you will find one suitable for use with that high AIC.
Loose with the language is not serving you here. It is NOT about the motor, it is about the EQUIPMENT ahead of it. All electrical devices that control the flow of POWER (as opposed to control circuits) must be capable of surviving a short circuit event without entering into a “RUDE” condition (Rapid Unplanned Disassembly Event). That applies to breakers, disconnect switches, fuses and fuse holders, terminals, contactors, overload relays, solid state power devices, EVERYTHING in the power circuit, EXCEPT the motor or load device (heater) itself. Fuses and circuit breakers already have that baked into their “interrupt ratings), commonly shown as “AIC”, and fuse holders generally are rated for the fuses they can hold. But the rest of it must be tested and listed with the breakers or fuses based on the “let-through” energy they allow before clearing the fault.So all motors [technically motor controllers, but I'm going to be loose with my language and say "motors"], all motors everywhere, always, should have their available fault current calculated and compared against the controller's SCCR?
if you get a 5kA SCCR label on a piece of commercial or industrial equipment, it can be next to impossible to connect it.
A current limiting fuse or breaker prevent or lessen itIf someone drops a wrench on live bus bars, you can have an arc event, no matter what the ratings of the equipment.
There will always be the arcing and always will be energy released by the arcing. Overcurrent devices can vary in how they react to the incident which will change how much energy is released in the arcing incident. Lower current but for longer time can have more incident energy than higher current for shorter time.A current limiting fuse or breaker prevent or lessen it
The question, always injury or fire by arcingThere will always be the arcing and always will be energy released by the arcing. Overcurrent devices can vary in how they react to the incident which will change how much energy is released in the arcing incident. Lower current but for longer time can have more incident energy than higher current for shorter time.
SCCR is about equipment and not directly about people protection. If the current in an incident doesn't exceed the SCCR of some equipment this mostly means that equipment should not be throwing shrapnel at you because it couldn't withstand the forces involved.The question, always injury or fire by arcing
of short-circuit cause
The intent SCCR prevent or lessen it
Failure it mean design failure
These terms are for locations which have not performed a complete arc flash study. They are commonly used as slang in our industry. For the past decade, the preferred NFPA 70E ratings would be expressed in APTV or calories/centimeter(squared).arcflash category to 1 or 0 mitigate
The failure is on the part of the installer when the equipment is connected to a circuit that has an available fault current that exceeds the SCCR of the equipment.The intent SCCR prevent or lessen it
Failure it mean design failure
Not concern PE?The failure is on the part of the installer when the equipment is connected to a circuit that has an available fault current that exceeds the SCCR of the equipment.
Hope op and winnie agree #52These terms are for locations which have not performed a complete arc flash study. They are commonly used as slang in our industry. For the past decade, the preferred NFPA 70E ratings would be expressed in APTV or calories/centimeter(squared).
Here's you one that wasn't a bolted fault or short circuit, but it burned long enough to take out a 480V 750KVA bank on a pole.
The cause was accumulated grinding dust with condensing humidity in the middle of a wet winter.
View attachment 2576786
If not someone needs updated training.Hope op and winnie agree #52
Assuming you mean Professional Engineer, there are far more installations designed and installed by contractors and electricians than ones designed by PE. And even there the mechanical and electrical PEs often don't talk to each other so equipment with SCCR far lower than the available fault current is specified by the mechanical engineer.Not concern PE?
A correspond between cal/sq.cm and arcflash catIf not someone needs updated training.
NFPA 70E dropped 'Category 0' some 10 years ago.
Slang is okay in most circumstances but it should not be misleading.