Service feed overcurrent protection for multi-unit EV charging

brian.1

Member
Location
Santa Clara county
Occupation
retired, BSEE, multiple home remodels including 120/240V wiring, computer programmer
My 20 unit condo building is adding EV chargers for all units and I'm looking for help managing the continuous EV charging load on my condo building's transformer and service feed wires.

There are 20 units each with a 2 phase 90A at 120/208V main breaker which gives a theoretical total of 1800A at 120/208V. IIUC that would be 1039A in 3 phase.

My condo building's service was set up long before EVs and EV charging was a consideration. As was standard at the time, the service was derated so the 3 phase service feed installed was 600A at 120/208V. The 600A is peak load. IIUC A continuous load can only be 80% of that which is 480A.

The plan is to limit each EV charging circuit current to 24A at 208V. This would give a total EV charging current of 480A at 208V which is just at the continuous rating for the service transformer and feed wires. This sounds great BUT the condos still need electrical power for other things like A/C, oven, lighting, etc. We could lower the EV charging current but how much? However, people are asking for more current not less. Besides, wouldn't it be rare for all EVs to be charging at the same time?

So 2 questions:
  1. How to detect 480A continuous, not 480A peak?
  2. How to disable or limit EV charging without interfering with a condo's normal power usage?
 
I will approve this once the OP clarifies
1. What was occupation before retirement?
2. Who is doing the electrical work?
It’s a good question that will be of interest

(answered in a different thread...unlocked)
 
Last edited by a moderator:
I will approve this once the OP clarifies
1. What was occupation before retirement?
2. Who is doing the electrical work?
It’s a good question that will be of interest

(answered in a different thread...unlocked)
From the other thread:
  • We will be using certified electricians. For insurance, it is important to have the work done by qualified people and done with permits.
 
If each unit were to draw 24A at 208V then the 3-phase line currents at the service would be approximately 277A which leaves you quite a bit of headroom without worrying about whether that full load would ever be continuous (which it almost certainly wouldn't, but you arguably still have to plan for).

You can also get units for each condo that would limit the EV charging draw if that unit were using a lot of power on other things. The jurisdiction will need to agree with the logic of what your doing in light of NEC load calculations, so limiting the draw on each unit to the existing 90A feeder rating may help.

There is a member on this forum @brycenesbitt who may be interested in helping you out. (Hope that's kosher to say here.) This sort of thing is his specialty and he's in the Bay Area.
 
Ok, thank you for pointing out my 1st error: the 20 units × 24A 2 phase EV charging = 480A 2 phase would only be 480A ÷ 1.732 = 277A for 3 phase. That definitely helps but the condos could still be drawing other power.

For the individual condos, the EV charging is reduced if the current in the condo's wiring is above the 80% of 90A = 72A. Still, 20 units × 72A = 1440A 2 phase which is 1440 ÷ 1.732 = 831A 3 phase. So still seems wise to have monitoring and protection.
 
There is a member on this forum @brycenesbitt who may be interested in helping you out. (Hope that's kosher to say here.) This sort of thing is his specialty and he's in the Bay Area.
Yes, EV Plugbox LLC is my firm, and does specialize in just this, thanks for the shout out @jaggedben

We do all the electrical calculations, engineering, permitting, incentive matching and installation.

Now we can't call it "diversity" any more, but indeed the concept formerly known as load diversity is something a project can take advantage of. But the case is weaker for EV charging than other fields, as it's entirely credible that everyone will plug in overnight and set cars to start at midnight (due to mindbogglingly dumb rate structures with PG&E). You can't depend on luck for electrical calculations.

For EV Plugbox projects:
In Campbell, Cupertino, Gilroy, Los Altos, Los Altos Hills, Los Gatos, Milpitas, Monte Sereno, Morgan Hill, Mountain View, Saratoga, Sunnyvale and Unincorporated Santa Clara County, we have funding that can pay for much or in some cases all of an installation EVEN for HOAs. Most incentive funding excludes all reserved parking, thus don't play well with the HOA ownership model.
 
Yes, EV Plugbox LLC is my firm, and does specialize in just this, thanks for the shout out @jaggedben

We do all the electrical calculations, engineering, permitting, incentive matching and installation.

Now we can't call it "diversity" any more, but indeed the concept formerly known as load diversity is something a project can take advantage of. But the case is weaker for EV charging than other fields, as it's entirely credible that everyone will plug in overnight and set cars to start at midnight (due to mindbogglingly dumb rate structures with PG&E). You can't depend on luck for electrical calculations.
Do you have a long term way to measure the building service feed's continuous current separately from the peak current?

If so, what does the system do if the continuous current is too high?
 
While I am waiting for thoughts from others, let me share my idea. I am not an expert in this area so my idea may or may not be a suitable idea and I'd appreciate constructive feedback.

The overcurrent monitors I've seen do not seem sufficient. They can trip if the current is above a set level but the ones I've seen only have a few seconds on-delay for motor starting. My understanding is the 80% overcurrent limit is for loads that run longer than 3 hours. If anyone knows of an overcurrent monitor that has a long on-delay please let me know.

Otherwise, here is my idea to detect continuous overcurrent (which is below the breaker limit):
  • Use an over current monitor to detect current above the 80% level.
  • Use an on-delay relay timer to register that the over current has been happening continuously for a while.
over current monitor.jpg
The 3 current transformers step down the 3-phase current to a range suitable to the current monitor.

The current monitor (eg, a Time Mark 2742-24) is set to trip when any of the 3-phase currents is above the 80% continuous current level. However, this trips if the current is over the 80% limit for more than 20 seconds. What is needed is to detect an over 80% for a longer length of time. For this I propose that the signal from the overcurrent monitor be passed to an on-delay relay timer.

When the signal to the on-delay relay (eg, a THL-8024U-42) is on, the on-delay relay starts a timer. Any time the signal drops the timer resets. Only if the signal is continuously on for the on-delay time does the output of the on-delay trigger. This only would detect over 80% and not detect how much over the 80% the current is.

I'm not sure what the on-delay time should be. I guess it could be 3 hours but because the amount over 80% is not measured, I'm wondering if the time should be shorter. Maybe an hour? Or 1/2 an hour?

This only detects the continuous overcurrent and does not address what should happen in response. Right now I will leave that discussion for later.

I welcome constructive feedback.
 

Attachments

  • over current monitor.jpg
    over current monitor.jpg
    13.3 KB · Views: 2
Do you have a long term way to measure the building service feed's continuous current separately from the peak current?
yes, with some buts.
our local jurisdiction tag locks the compartment with the conductors.
we are working on getting a formal rule change to allow access to place ct clamps in what's called the green book.
 
yes, with some buts.
our local jurisdiction tag locks the compartment with the conductors.
we are working on getting a formal rule change to allow access to place ct clamps in what's called the green book.
Thank you. That is very interesting information.
 
Anyone have any thoughts on this? ie:
  • Would this design work?
  • Any improvements?
  • Would tripping at 1 hour be a reasonable or good choice?
  • Are there different designs?
 
yes, with some buts.
our local jurisdiction tag locks the compartment with the conductors.
we are working on getting a formal rule change to allow access to place ct clamps in what's called the green book.
That would be great. A lot of panels are difficult or impossible to install CT's in.
 
Anyone have any thoughts on this?
My question is where are you going with this? You can theorize all you want, but unless you have deep pockets or can get backing for research and development, no matter how good you think your idea is it's going nowhere. Without listing and approvals nobody is going to want to touch it- unless you build it and market it in China. Consider also that there are solutions to your "problem" already out there. As has been pointed out, there are companies that will install a substation with a separate new service and chargers on your condo property for the 20 units at little or no cost. They will get their revenue from the people who use them.

And charging has to be done outside, or at least it should be if you don't want your parking garage to burn down.

-Hal
 
As has been pointed out, there are companies that will install a substation with a separate new service and chargers on your condo property for the 20 units at little or no cost. They will get their revenue from the people who use them.
That's basically a tax on apartment residents. Profit for a company on back of the renters.
 
I welcome constructive feedback.
You are reinventing a wheel that's well developed.

Minor excursions over 80% are not a problem, because heat's the problem not current.
Start with actual measurements from your building.
Then look at optimizing other loads.
There is likely plenty for as much EV as your residents can handle.
 
My question is where are you going with this?
Thank you for the question.

Today we protect electrical wiring for peak current with circuit breakers and for continuous current with derating. These are both inexpensive and effective.

Here is what I see:
  • Existing condo buildings' electrical systems were not designed with EV charging requirements.
  • Existing condo buildings' circuit breakers protect peak current but not continuous current.
  • Existing condo buildings' electrical systems have enough current for a few EV chargers but may not have enough current for every unit.
  • Existing condo buildings' electrical systems could be upgraded with a new transformer but my understanding is that costs $50K or more.
  • I see continuous power management systems starting in the $15K range; eg, RVE HUB
  • Today I see condo buildings are adding a few EV chargers but rarely for every unit.
  • If 3 condo owners wanted to add EV charging, adding continuous power management would add $5K for each of them.
  • Asking a few condo owners to each pay something like $5K or more extra to cover a continuous power management system (much less a new transformer) for the entire condo building is too much to ask them.
  • If every unit were adding EV charging it would be prorated over a larger number and thus less of a problem.
  • Over time more and more EV chargers are going to be added but who is paying attention to the continuous power? I can do it for my building for now but what happens if I'm not there?
Right now condo buildings are adding EV charging completely unaware of the continuous power issue and without a reasonably priced way to monitor it.

I am looking for a modestly priced (less than $1K) way to silently monitor the continuous power so if/when the continuous power is too great, condo buildings can know when they need to add a continuous power management system.

Brian
 
I am looking for a modestly priced (less than $1K) way to silently monitor the continuous power so if/when the continuous power is too great, condo buildings can know when they need to add a continuous power management system.
Brian
As this thread has covered, that's an off the shelf thing. I install and support exactly such systems in the San Francisco Bay Area, mostly for apartments, but for condos also. You appear to be a condo owner I'd guess from your questions.
 
I am looking for a modestly priced (less than $1K) way to silently monitor the continuous power so if/when the continuous power is too great, condo buildings can know when they need to add a continuous power management system.
Do you have smart meters on the building and does the utility keep 15 minute interval usage data per meter? If so, and you can get that for all units, all you need to do is sum the loads of each unit together if they use the same time intervals (assuming the car charges are coming off of each units panelboard) and check the total KW being drawn. This is like what you do in 220.87 to do a load calc based on usage instead of overly conservative calculations.

Not sure if the poco would turn over each individual's power history to a condo board, so may need to have each owner give permission to give it out. If the poco doesn't have this data, then it isn't a solution, but you could possibly put some power recording device on the service to measure it. Someone needs to read the data monthly or quarterly to see what the loads are. Continuous loads are a bit tougher to measure as 220.87 data asks for 15 minute intervals. You would need to find the worst case 12 consecutive intervals to get a continuous number. Probably doable with an Excel file, and my poco provides the data in excel format directly.

I also wonder about your assumptions in post 1. A 90A breaker to a unit doesn't mean their load calc is 90 amps. How did you determine it was a 600A service? Did you see multiple 200A breakers in meter stacks and add them up, or is there a single 600A main, or did you examine the service conductor size to see what it is. If there are multiple service disconnects, they are allowed to sum to larger than the calculated service and most likely are. The service conductor must be sized to the calculated load, not the sum of the main breakers when there is more than one.
 