230.71(A)(1) One- and Two-Family Dwellings.
Service disconnects shall be installed in a readily accessible outdoor location in accordance with one of the following:
- On the dwelling unit
- Within sight of the dwelling unit in accordance with 110.29
Exception: The service disconnect shall not be required to be installed on or within sight of the dwelling unit when an emergency disconnect is installed in accordance with 225.41.
230.70(B) Service Disconnect Marking.
Service disconnects shall be marked in accordance with 230.70(B)(1) and 230.70(B)(2).
(1) Marking.
Service disconnects shall be marked “SERVICE DISCONNECT.” The marking shall be on or adjacent to the service disconnect and comply with 110.21(B).
(2) One- and Two-Family Dwellings.
Enclosures of disconnects for one- and two-family dwellings shall be marked as follows: “EMERGENCY DISCONNECT.”
Markings shall comply with 110.21(B) and both of the following:
- The markings shall be located on the outside front of the disconnect enclosure with a red background and white text.
- The letters shall be at least 13mm (1⁄2 in.) high.