I have to run #6 NM through the basement 50 feet through block transition to PVC for 30 feet up in garage panel. Can I run the #6 NM all the way? Or should I run THWN through conduit to garage?
 
I have to run #6 NM through the basement 50 feet through block transition to PVC for 30 feet up in garage panel. Can I run the #6 NM all the way? Or should I run THWN through conduit to garage?
Your title says NM in conduit, but your question seems to be different. If you're asking if you can run the NM through the basement without conduit, then yes you can. If the basement is open, you can strap the NM to the underside of the floor joists. The NM just needs to be secured and out of the way of physical damage.
 