I have a customer that is wanting an sccr rating of 45ka. The issue is the Yaskawa drives lowering the rating to 35ka. Speaking with Yaskawa, I can use a different fuse that would bring this to 42ka.
Question, other than an isolation transformer, how can I raise the overll SCCR rating? Can I put a branch disconnect in front of the drive fuses??? Would this circuit now be rated at the kva of the disconnect???
Feeder Circuit | | | |
E7LRL36600U31X | SQ D BREAKER 600V 600A 100KA SCCR | 100KA | |
Control Transformer | | | |
E5LPCC15 | BUSSMANN FUSE CLASS CC 15 AMP | 200kA | |
E5811-421 | WAGO FUSE HOLDER CLASS CC 2P | 100kA | |
E363322308 | SOLA TRANSFORMER REG 3KVA 600V 60HZ | 1200A | |
General Transformer | | | |
E5LPCC30 | BUSSMANN FUSE CLASS CC 30 AMP | 200kA | |
E3HS10F7.5AS | SOLA TRANSFORMER 7.5KVA 600V 60HZ | 3970A | |
Chain Rail Temp | | | |
E5LPCC20 | BUSSMANN FUSE CLASS CC 20 AMP | 200kA | 4600A |
E5811-431 | WAGO FUSE HOLDER CLASS CC 3P | 100kA | |
E920403 | HUBBELLOCK RECEPT 30A,600V | 10kA | |
E921415B | HUBBELLOCK M PLUG 30A,600V | 10kA | |
Vacuum Pump | | | |
Heat Tunnel | | | |
E5LPCC10 | BUSSMANN FUSE CLASS CC 10 AMP | 200kA | |
E5LPCC20 | BUSSMANN FUSE CLASS CC 20 AMP | 200kA | |
E5811-411 | WAGO FUSE HOLDER CLASS CC 1P | 200kA | |
E7SOI885070 | CELDUC SSR 600V 50A, CURRENT SENSE | 100kA | |
E92010-1201 | WAGO 2C TRM GRY 20-6 AWG 51A | 100kA | |
E92004-1201 | WAGO 2C TRM GRY 20-6 AWG 51A | 100kA | |
E92002-2201 | WAGO 2C DBL-STK GRY 22-12 AWG 20A | 100kA | |
E92006-1201 | WAGO 2C TRM GRY 20-10 AWG 30A | 100kA | |
Top Platen Drive* | | | |
E5LPJ50SP | BUSSMANN FUSE CLASS J 50 AMP | 300kA→35kA | 4300A |
E5CH60J3I | BUSSMANN FUSE HOLDER CLASS J 3P | 200kA | |
E3SGDV-370D01A | YASKAWA S5 DRIVE 400V 15KW | 5kA | |
Bottom Platen Drive* | | | |
Index Drive* | | | |
Plug Drive* | | | |