I saw an existing building has a tap on conductor of secondary side of transformer. see picture.
I know it is code violation per NEC (2008)
240.21
(C) Transformer Secondary Conductors. A set of conductors
feeding a single load, or each set of conductors
feeding separate loads, shall be permitted to be connected
to a transformer secondary, without overcurrent protection
at the secondary, as specified in 240.21(C)(1) through
(C)(6). The provisions of 240.4(B) shall not be permitted
for transformer secondary conductors.
My question is: since it is old building, I wonder if there any older code allow to do as picture show?

	
		
			
		
		
	
				