Cranetb_Newell
- Newville, PA
- Electrical Engineer
We currently have some Start/Stop control stations on our Sorter Downlane conveyors to start and stop each individual downlane. When the manufacturer installed the system, they used the AB 800FP-E4PX01 for the Stop pushbutton, which has the extended head.
Unfortunately, the employees have been hitting the Stop pushbutton accidentally when grabbing the cartons off the line, so we wanted to protect the Stop Pushbutton in some way, likely replacing with either the G4PX01 (Guarded) or F4PX01 (Flush) versions of the pushbutton.
However, we are now getting pushback from our Safety Department that “Stop” pushbuttons need to have an extended head, be continuously operable, and readily accessible. They are quoting the following:
- ANSI B11.19 Section 9.4.1: "Normal stop function. Stop functions shall meet the requirements of NFPA 79."
- NFPA 79 Section 10.2.1: "Pushbutton Actuators. Pushbutton actuators used to initiate a stop function shall be of the extended operator or mushroom-head type."
- NFPA 79 Section 10.7.1.1: "Stop and emergency stop pushbuttons shall be continuously operable and readily accessible."