Would this be a accurate description?
Most start capacitors have a much higher MFD (microfarad) rating than the run capacitor, meaning they can store and release much more current. They are also generally electrolytic capacitors instead of oil-filled metal film-type, like a run capacitor.
All this adds up to a start capacitor being able to store and release a lot of current into the start winding, but it only stays in the circuit for a short period of time without damaging itself because it cannot dissipate heat easily like the metal film run capacitor.
The start capacitor is wired in parallel with the run capacitor, as shown in the image above. The potential relay contacts are closed on startup, which means the capacitor is in the circuit with all that electron storage capacity. When the compressor contactor closes, a large amount of current can move into that start winding because there is a larger “membrane” (see
part 1 of this series) that can store and release energy. This extra current moving through the start winding helps get the compressor started more quickly,
But the start capacitor must be pulled out of the circuit very quickly to avoid overheating itself or damaging the compressor start winding.
Single-phase compressor start windings are not designed to carry high continuous current like the run winding. If the start capacitor were to stay in the circuit too long, the current on the start winding will stay high and risk damaging the start winding.
Various types of relays and controls can remove a start capacitor from the circuit, but the most common is a potential relay. The potential relay coil is either connected between start and common or start and run, and it is sized to open up when the motor reaches about 80% of its full speed.
The potential relay opens based on an effect called “Back EMF,” which leads us to our next thought experiment.