hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have 30kva transformer delta to wye. Primary voltage 380v three phase and secondary voltage 208/120v. Primary breaker is sized 40A and secondary breaker is sized 100A. Wverything is upto NEC 2017 this far.
The secondary side total demand amps comes to 99A. It wont trip the secondary 100A breaker but the total demand kvA comes to 99*.208.1.732= 35kva.
So question 99A demand wont trip the secondary breaker 100A but wont 30kva transformer be undersized due to 35kva demand load?
The secondary side total demand amps comes to 99A. It wont trip the secondary 100A breaker but the total demand kvA comes to 99*.208.1.732= 35kva.
So question 99A demand wont trip the secondary breaker 100A but wont 30kva transformer be undersized due to 35kva demand load?