2 questions
My nephew has a summer camp with an old 100 amp service. The only load to speak of is a standard electric range and an electric water heater. The 100-amp Murray panel is fine, and I would like to keep it.
The issue is that the SE cable is starting to deteriorate (overhead service) and the meter socket is hanging loose as the siding guys cut the screws when they resided it and it should have ground rods (it does have a copper water line more than 10' to the well). The other issue is the drip loop is too low, so it needs a mast.
So I would like to keep the panel , put up a mast and ground rods and a new meter socket.
Would I have to go with a meter main/ emergency disconnect? So what constitutes a service change that would require an emergency disconnect?
2d question. About 25 years the 100 amp main breaker went bad (same job). I went to the supply house and bought a two pole Murray 100amp breaker and installed it.
I didn't realize until I put the breaker in that the switch position was reversed. The breaker mounts vertically. The old breaker up was on and down was off as it should be. The replacement is down on and up is off.
My nephew has a summer camp with an old 100 amp service. The only load to speak of is a standard electric range and an electric water heater. The 100-amp Murray panel is fine, and I would like to keep it.
The issue is that the SE cable is starting to deteriorate (overhead service) and the meter socket is hanging loose as the siding guys cut the screws when they resided it and it should have ground rods (it does have a copper water line more than 10' to the well). The other issue is the drip loop is too low, so it needs a mast.
So I would like to keep the panel , put up a mast and ground rods and a new meter socket.
Would I have to go with a meter main/ emergency disconnect? So what constitutes a service change that would require an emergency disconnect?
2d question. About 25 years the 100 amp main breaker went bad (same job). I went to the supply house and bought a two pole Murray 100amp breaker and installed it.
I didn't realize until I put the breaker in that the switch position was reversed. The breaker mounts vertically. The old breaker up was on and down was off as it should be. The replacement is down on and up is off.