Homeowner has 5 A/C condensing units located outside at ground level. There is a panelboard directly adjacent to all of the units. All units are within sight of the panelboard.
All of the unit nameplates call for "Max Fuse / Max C.B.", so a fuse is not mandatory per the manufacturer nameplate. The breaker ratings match the MOCP.
Do the circuit breakers in the panelboard qualify as the local disconnect for the unit?
Is this code compliant, or is an additional local disconnect required for each unit?
All of the unit nameplates call for "Max Fuse / Max C.B.", so a fuse is not mandatory per the manufacturer nameplate. The breaker ratings match the MOCP.
Do the circuit breakers in the panelboard qualify as the local disconnect for the unit?
Is this code compliant, or is an additional local disconnect required for each unit?