TwistLock
 - California
 - Electrician
As you can only use / re-identify the white insulation/neutral in an NM cable as the supply to a switch loop per 200.7(C)(2), so then I assume you can not (example) use a 10/2 NM cable, with black / white conductors, for 240v branch circuit by identifying the white as an ungrounded conductor.   So I thought the workaround was using a 10/3 NM cable and capping off the white wire both ends & just using the black/red (no EVSE outlet, say perhaps HVAC).  Except I read(?)that 300.3(B) prohibits this too.
But then we get into 404.4(C) and the neutral is capped, not terminated, at the switch box and intended for future use. So why can’t an unused neutral in my 10/3NM 240v circuit be categorized as a functional spare?