I have customer who called me for an unrelated project. While there I found that the contractor who built a “Tiny house” for an AirB&B ran a single 12/2 Romex in flexible nonmetallic 1/2 PVC conduit from the panel over the roof of the primary home down the back side, under ground and came up under the tiny house. Then out of the pvc “bare Romex for a single circuit to run the whole place.
The customer mentioned that guest trip the breaker often and the owner had to remove the provided hairdryer prevent tripping.
Going over the roof is still the most practical route to bring the new feeder over. The roof is flat tar and gravel. Planning to use 1” EMT.
I have not encountered this specific situation before. From what I have read, EMT conduit with rain tight fittings is acceptable, but the question is how to secure the 40 ft run. Do I need to secure the EMT to the roof every 10ft or secure the EMT to blocks that can move to allow for expansion?
Secondly, is a pressure treated 4x4 block of wood acceptable or should a listed support device be used?
The customer mentioned that guest trip the breaker often and the owner had to remove the provided hairdryer prevent tripping.
Going over the roof is still the most practical route to bring the new feeder over. The roof is flat tar and gravel. Planning to use 1” EMT.
I have not encountered this specific situation before. From what I have read, EMT conduit with rain tight fittings is acceptable, but the question is how to secure the 40 ft run. Do I need to secure the EMT to the roof every 10ft or secure the EMT to blocks that can move to allow for expansion?
Secondly, is a pressure treated 4x4 block of wood acceptable or should a listed support device be used?