Xfrmr Voltage
Could be the supply system is 3 phase, 3 wire, 480 volts without a neutral. The tranformer with the Wye secondary creates a neutral.
It could be a dedicated isolation transformer. Maybe the load is sensitive to power quality issues.
But based on it being a called an LP panel, I agree with infinity.
Yeah, I saw LP and assumed lighting panel which would make sense for 480Y/277 volts.
Another possibility would be to address a high fault current situation but my money would be on Post #2
FIFY. :D
Even if the service is 480/277V and the transformer is wye-wye, the neutral on the primary side should not be connected.
If it is actually a wye-wye transformer (rare, but possible), then you will need to connect the primary neutral to get stable L-N secondary voltage.
If it is a 480/277 source, then the question is, why is there a transformer to feed a “lighting panel”? You already had 277V for the lighting…
As I mentioned in Post #6, I have seen that fairly often where the available fault current at the 480 panel is extremely high and transfgotmer is added to provide a source of power to address low SCCR or breaker AIC.