I’m looking to get confirmation I am interpreting the nec correctly, and the plan I have came up with for a 4 space possibly in future 6 space rv site doesn’t have any faults…
My plan is to put a 200amp feed through 8 space panel at the pole under the poco meter.
I would use the feed through lugs and run 3-250aluminum, 1-3/0aluminum quad plex in 2-1/2 pvc to first RV pedestal and then jump out the next three using the lugs at the bottom… (all 4 sites are equipped with 50,30,20amp receptacles)
There will also be a main lug 100amp remote distributing panel fed from a 100amp breaker at the service. The 100amp remote distribution panel will be fed with 3-1/0 al and 1#2al quad plex in a 2” pvc conduit. This panel will be feeding a 2hp well and possible heater.
I was told well motor is 3 phase, and they will be adding a phase converter. I will need to supply wire rated at 1.25% of the well motor. 2 hp 3 phase 230 volt motor should pull 6.8amps
6.8amps x 1.25 = 8.5amps. After looking at Franklin aims Manuel. I thought I could run 2pole 20a ocod with #12 copper conductors down to the well pressure switch/ phase converter. Ocpd to pressure switch is less than 25 ft, and the well is 200ft down. I’m assuming we’ll company will run #10 or larger down to well motor and pump.
I used the aims Manuel to come up with this for voltage drop.
#12 copper is good for 510 feet according to there chart
#10 copper is good at 810 ft
25ft/510=0.588 in .0438 branch circuit distance
220ft/810ft =0.2716 well leads
If you add these numbers together and multiply by 100 you get 31% so I would still have another 69% to go before I’m over the 5% voltage drop….
Do I need to
Include the feeder wires coming from main disconnect to remote distributing panel?
I came up with this by using the demand factors listed in 551.73(A)
12,000va X 4sites = 48,000va
48,000va X .75%demand= 36,000va
36,000va / 240 volts = 150 amps
If they end up adding two more sites in future
72,000va X 60% demand= 43,200va
43,200va / 240volt = 180 amps
Questions:
Is my 200 amp service big enough for 4 sites and the well. If they add a total of 6 site will my service still be big enough?
Do my tv pedestals need to be rated 200 amp to feed through 4-6 pedestals. This is the model I’m thinking of telling the rv site owner he needs to get. M675CP6010 I will provide de cut sheet in the pictures. RV pedestals will not have main breaker
Thank you to all on this page that inspire to learn and teach! I appreciate you very much!
My plan is to put a 200amp feed through 8 space panel at the pole under the poco meter.
I would use the feed through lugs and run 3-250aluminum, 1-3/0aluminum quad plex in 2-1/2 pvc to first RV pedestal and then jump out the next three using the lugs at the bottom… (all 4 sites are equipped with 50,30,20amp receptacles)
There will also be a main lug 100amp remote distributing panel fed from a 100amp breaker at the service. The 100amp remote distribution panel will be fed with 3-1/0 al and 1#2al quad plex in a 2” pvc conduit. This panel will be feeding a 2hp well and possible heater.
I was told well motor is 3 phase, and they will be adding a phase converter. I will need to supply wire rated at 1.25% of the well motor. 2 hp 3 phase 230 volt motor should pull 6.8amps
6.8amps x 1.25 = 8.5amps. After looking at Franklin aims Manuel. I thought I could run 2pole 20a ocod with #12 copper conductors down to the well pressure switch/ phase converter. Ocpd to pressure switch is less than 25 ft, and the well is 200ft down. I’m assuming we’ll company will run #10 or larger down to well motor and pump.
I used the aims Manuel to come up with this for voltage drop.
#12 copper is good for 510 feet according to there chart
#10 copper is good at 810 ft
25ft/510=0.588 in .0438 branch circuit distance
220ft/810ft =0.2716 well leads
If you add these numbers together and multiply by 100 you get 31% so I would still have another 69% to go before I’m over the 5% voltage drop….
Do I need to
Include the feeder wires coming from main disconnect to remote distributing panel?
I came up with this by using the demand factors listed in 551.73(A)
12,000va X 4sites = 48,000va
48,000va X .75%demand= 36,000va
36,000va / 240 volts = 150 amps
If they end up adding two more sites in future
72,000va X 60% demand= 43,200va
43,200va / 240volt = 180 amps
Questions:
Is my 200 amp service big enough for 4 sites and the well. If they add a total of 6 site will my service still be big enough?
Do my tv pedestals need to be rated 200 amp to feed through 4-6 pedestals. This is the model I’m thinking of telling the rv site owner he needs to get. M675CP6010 I will provide de cut sheet in the pictures. RV pedestals will not have main breaker
Thank you to all on this page that inspire to learn and teach! I appreciate you very much!