I'm looking to upgrade my tank farm at my new facility, and the existing conduit is currently secured to the process piping. This is causing it to break at the threads in some areas due to the flooding and vibrations. They have a mixture of supports constructed of Unistrut with all-thread wrapping around the process piping and short extensions of Unistrut that are attached to other conduits for support. I also noted that there are no low point drains and was seeing if anyone could help me pin some of these issues out in the code book to aid me in writing a proposal.
TmO: I apologize for suggesting solutions rather than responding to what you are actually asking for.
"... seeing if anyone could help me pin some of these issues out in the code book to aid me in writing a proposal."
Yes, we could help you pin down some of these issues, but it is likely you would focus on what you notice rather than other possibly more critical items. Believe it or not, your company's insurance carrier may do much for you by sending an inspector, free of charge. I have done so with great results in areas I didn't understand well, such as gas burners.
These references are from NEC 2020. You will need to read them carefully to have a complete understanding. After doing so, it is likely that some things that you didn't realize are a violation of the Code actually are:
Article 344 Rigid Metal Conduit Type RMC
Article 500 Hazardous (Classified) Locations, Classes I, II, and III, Divisions 1 and 2
Article 501 Class I Locations
Not trying to brush you off, guy. Just don't want you to miss important stuff like using sealtite between a device and a seal, just as an example.