I'm installing a 400 A CT service for one of my better customers this week and I've never done one before. The utility here provides the cabinet, CT's, and meter. I got them yesterday. The change over is scheduled for this Thursday and has been on the books for two plus months. This service comes to a private pole where the existing 200A meter is located. The plan is to reuse the existing feeders going to the house and we've run new 2" PVC to the detached garage and pulled 4/0, 4/0, 2/0 URD to a new 200A panel.
I met with a planner from the utility (he's the one that suggested the CT service) two months ago who signed off on my plan. He's been unavailable since then.
Going over the paperwork provided with the equipment, they require that the service neutral and CT cabinet be bonded to ground in the CT cabinet. Does this ground then become the GEC?
My boss and I have been going back and forth on this one but, I would like to add two 200 A disconnects on the pedestal on the load side of the CT cabinet. But if I do this wouldn't I be required to pull a ground with my feeders, or is there a way around this?
You're help is greatly appreciated.
I met with a planner from the utility (he's the one that suggested the CT service) two months ago who signed off on my plan. He's been unavailable since then.
Going over the paperwork provided with the equipment, they require that the service neutral and CT cabinet be bonded to ground in the CT cabinet. Does this ground then become the GEC?
My boss and I have been going back and forth on this one but, I would like to add two 200 A disconnects on the pedestal on the load side of the CT cabinet. But if I do this wouldn't I be required to pull a ground with my feeders, or is there a way around this?
You're help is greatly appreciated.