Deltaforce
- India
- Electrical Engineer
Renewable Energy Systems solar, wind powerWhat is RES?
I took it to mean Renewable Energy Systems. (A Communist plot to weaken America)What is RES?
You got me on that one. To be fair to myself I was seizing the opportunity to make fun of the NEC and didn't check the relevant code section.Hmmm, I would say the demand numbers would be fine. Here is what the relevant sections say:
230.90 Exception No. 3: Two to six circuit breakers or sets of fuses shall be permitted as the overcurrent device to provide the overload protection. The sum of the ratings of the circuit breakers or fuses shall be permitted to exceed the ampacity of the service conductors, provided the calculated load does not exceed the ampacity of the service conductors.
220.87 Determining Existing Loads. The calculation of a feeder or service load for existing installations shall be permitted to use actual maximum demand to determine the existing load under all of the following conditions:
I don't think anything in 220 has to give us permission to use 220.87, if it did, I dont think we could ever use it.
Yes.So on a 225 amp service, I can put two 200 amp, and four 100 amp breakers in it and call it a day?
My observation is ever since they came out with the QOM series mains type back in late 80's or early 90's that information on the label fixed inside of panel has said something to the effect they are suitable for service equipment when a main breaker is used on most or maybe even all of them.That is wrong.
They have always said a single main OR not more than 6 breakers.
All QO single and three phase and HOM load centers are marked as "Suitable for use as Service Equipment" if equipped with integral main breaker or when not more than six disconnecting means are provided
Am I missing something here? how are you going to put Six 3 pole breakers in a box with only 12 spaces? 12divided by 3 equals 4.Something like this
Can the sum total amperage of the breakers exceed the amperage of the service?
Using this panel for example, could you install six 25 amp 3 phase breakers for a total of 150 amps? And if so, what are the limitations and can the sum of the amperage exceed the rating of the service conductors also?
oops, used the wrong example. Not the box I was planning on anyway. But even if I balance the loads a little differently and have 2 single phase 240 feeders for the lights and receptacles I'm going to need an 18 space because it's an open delta high leg so there will be empty spaces.Am I missing something here? how are you going to put Six 3 pole breakers in a box with only 12 spaces? 12divided by 3 equals 4.
Oh its your building, man if it were my building ..This is my own building so I want to put a lot of thought and planning into it.
Not want to put whole house protection spd?This is my own building so I want to put a lot of thought and planning into it. Everything is operating now without a problem,
All QO single and three phase and HOM load centers are marked as "Suitable for use as Service Equipment" if equipped with integral main breaker or when not more than six disconnecting means are provided and the panelboard is not used as a lighting and appliance branch circuit panelboard.Here is a link to the SE website
Yeah i still see that all the time, im like ya know thats not a thing anymoreand the panelboard is not used as a lighting and appliance branch circuit panelboard..
Why is this a problem? If there is no definition then this exception can't exist.Other problem here is NEC eliminated the "lighting and appliance panelboard" quite some time ago now.
Whats wrong with having a service gutter and a tap to a 3-phase 240 panelboard and a tap to a single phase 120/240 panelboard each with a main? That is still allowed.
Well 4 of the fused disco's already feed panels in other parts of the building. so that would require moving all their branch circuits the other 2 fused discos run an air compressor and a welder those two would be easy to moveWhats wrong with having a service gutter and a tap to a 3-phase 240 panelboard and a tap to a single phase 120/240 panelboard each with a main? That is still allowed.