NEC Continuous and Non-Continuous and System Size

kerrys914

Member
Location
St. Louis
Occupation
Engineer
Is the below correct?

320amp (400amp max) Meter Center Application

Lets say I have 350amps load on my 400amp MDP.
200amp continuous loads
150amp non-continuous loads

Will the 320amp meter center/socket be a correct application? My understanding as long as the continuous load is 320 or less and the combined loads (non + continuous) is 400amps or less, the 320amp meter will be fine.

Cheers
 
The check is 125% * continuous plus 100% * non-continuous <= 400A.

So 200*125% + 150 = 400, maxed out but OK.

Change your example to 250A continuous and 100A non-continuous, and it's no longer OK.

Cheers, Wayne
 
Thanks.. I also assume the 320amp meter center is okay since the 200amp*1.25% = 250amp (continuous load only) which is less then the 320amp meter socket rating for continuous load.
 
My understanding as long as the continuous load is 320 or less and the combined loads (non + continuous) is 400amps or less, the 320amp meter will be fine
That is correct*. See post 6.
 
Last edited:
That is correct.
I don't think so as stated. Per my example, if you have 250A continuous and 100A non-continuous, that satisfies both "continuous <= 320A" and "total <= 400A", but the required minimum rating is 125% * 250A + 100% * 100A = 413A, which exceeds the 400A rating.

Unless meter ratings behave differently from breaker ratings?

Cheers, Wayne
 
I don't think so as stated. Per my example, if you have 250A continuous and 100A non-continuous, that satisfies both "continuous <= 320A" and "total <= 400A", but the required minimum rating is 125% * 250A + 100% * 100A = 413A, which exceeds the 400A rating.

Unless meter ratings behave differently from breaker ratings?

Cheers, Wayne
Yes I left out the part where the continuous loads would have to be valued at 125%. My response should have been yes when it's continuous*125%+ the non-continuous.

So 320 amps continuous+ 0 non-continuous would be the maximum load permitted. For every amp the you reduced that 320 figure you could add 1 amp non-continuous.
 
So 320 amps continuous+ 0 non-continuous would be the maximum load permitted. For every amp the you reduced that 320 figure you could add 1 amp non-continuous.
For every amp you reduce the continuous figure below 320A, you can increase the non-continuous figure by 1.25A.

Cheers, Wayne
 
HA!!
Just to clarify as it got confusing

Keeping the numbers the same below (I should have used 90amps non-continuous to make this sample under 400amps):

200amp continuous load "connected" is 200amp*125%=250amp "calculated load"
250amp is <320amp meter base rating for continuous load....All good here

Add in non-continuous load of 100amps

250amp + 100amp = 400amp max system load.

A 320amp meter center feeding a 400amp MDP meets NEC.
 
200amp continuous load "connected" is 200amp*125%=250amp "calculated load"
250amp is <320amp meter base rating for continuous load....All good here
No. Because you used a 125% factor on the continuous load, you compare the result to 400A, not 320A.

If your load is all continuous, then you instead compare the continuous load (no 125% factor) to 320A. Because 320A * 125% = 400A, so that comparison is the same as the comparison in the previous paragraph.

If you have both continuous and non-continuous loads, then the check is as specified in my first post.

Cheers, Wayne
 