Typical number of strands #10 AWG Copper
brycenesbitt
United States
Without asking Gemni, how many strands are typical for #10 cable?
I was doing a build in a UL508A facility and all the #10 wire they had was very fine stranded, and was a royal PITA to get into the lugs cleanly.
I brought some 19 strand wire and that was fine. Are there other strand counts available (I've never cared before ;-)
7 and 19 are Class B and C stranding respectively per Chapter 9. Table 10. Standard terminations are only suitable for conductors with Class B and C standing. 37 strands is also a common stranding for 10AWG, especially if it is MTW.
Note that the stranding in post 3 does not match up with that in Chapter 9, Table 10.
Here's are pictures of the actual terminals involved.
It looks like a good design in that the curved element will gather strands rather that have them spread out over time.
The UL508A shop only had the fine strand wire: we went through their entire inventory, same stuff. Had to go get my own.
In olden times (1981) there was:
for 10AWG, 37/26AWG, 49/27AWG and 105/30AWG
for 12AWG, 7/20AWG, 19/25AWG, 65/30AWG, 165/34AWG
Each with slightly different resistance (but times have changed).
This is what ferrules are for. We ferrule pretty much everything when we build control panels precisely because of the fine stranding of the MTW wire we use. Get a ferrule kit and a good crimper.
SceneryDriver
Is that just for Ferrules?
In general for attaching crimp ends, ring crimps, etc.... what's the most bulletproof thing out there?
I've seen too many failed crimps (not ferrules) to have much comfort with them.
This crimper is just for ferrules, up to approximately 5awg (it's actually a metric tool).
This crimper, or one like it works well for insulated rings/forks, spades, etc...
Uninsulated crimps are harder to find tooling for, and are sometimes mfg. specific.
The important thing is to use a controlled-cycle tool, that ratchets and won't let you release until the crimp is complete. They also prevent over crimping if you have gorilla hands.
Do NOT use a tool like this for... anything really:
I honestly can't believe they're still made. Harbor Freight sells these kind of stripper/crimpers too, and they're even worse.
SceneryDriver
My application is for un-insulated crimps (nothing else is insulated, so why bother insulating the crimp, when it makes it harder to inspect
the crimp quality....
Any recommendations for a good insulated crimp tool? Brazed crimps vs. open?
I did see a decent video with pull tests on ratcheting crimp tools. The video is too long, but I liked the pull tests:
https://youtu.be/5fRRUSmG7LU?si=KeWUiux7oNq981dB