Service and other enclosures

Therealcrt

Senior Member
Location
Kansas City
Occupation
Electrician
I’m reading 250.92 and 250.96 and 250.97 250.92B says that if basically reducing washers are used or oversize concentric or eccentric knockouts, they would need a bonding bushing at the service regardless of the voltage of the service. 250.97 basically says if any circuit is over 250 V to ground and the enclosure encounters a concentric or eccentric knockout it’s not encountered then a standard EMT connector or listed fitting will be sufficient enough and not require a bonding bushing at those enclosures, even though some people still put them on which is OK but not needed so does that mean that any conduit that has a circuit in it over 250 V to ground? And it enters an enclosure with concentric or eccentric knockouts or reducing washers then it would need a bonding bushing to that enclosure.? For instance if I run a piece of conduit from a panel up to a junction box and I enter that junction box to a concentric or concentric knockout and it’s got 277 V for lighting. I need to put a bonding bushing on the inside of that connector inside the enclosure and bond it to the enclosure, correct?
 
so does that mean that any conduit that has a circuit in it over 250 V to ground?
The requirement is based on the conductor voltage within the raceway.
For instance if I run a piece of conduit from a panel up to a junction box and I enter that junction box to a concentric or concentric knockout and it’s got 277 V for lighting. I need to put a bonding bushing on the inside of that connector inside the enclosure and bond it to the enclosure, correct?
Most 4" or 4 11/16" metal boxes are listed for bonding over 250 volts even with concentric or eccentric KO's so no bonding bushing is required.
 
The exception to 250.97 allows you to use boxes with concentric/eccentric knockouts which are listed for such use without additional bonding. Most, if not all, "standard" (4" sq, 4=11/16, etc) boxes are listed as such.
 
Top