For ungrounded systems requiring ground fault detectors for ungrounded systems operating at not less than 120 volts and at 1000 volts or less, does this factor in whether "operation" is factoring utilization secondary or supply primary?
In other words as long as primary or secondary exceeds 1000 volts we no longer are required to install ground detectors?
An old ungrounded delta transformer i worked on was 4500 vac primary to 480 VAC secondary. The system did not have ground fault detectors. I assume this set up was correct because the primary side of the system exceeded 1000 vac. Is this correct?
The code doesnt destinguish the primary from the secondary portion of the system.
In other words as long as primary or secondary exceeds 1000 volts we no longer are required to install ground detectors?
An old ungrounded delta transformer i worked on was 4500 vac primary to 480 VAC secondary. The system did not have ground fault detectors. I assume this set up was correct because the primary side of the system exceeded 1000 vac. Is this correct?
The code doesnt destinguish the primary from the secondary portion of the system.