A cord and molded plug window hvac unit is going in a greenhouse for temperature control. The plug has a ground fault device similar to a hair dryer with a test and reset button.
It will need a 20 amp 240 volt receptacle to run on.
This being a wet location I will be installing a weatherproof box and weatherproof in-use cover and that brings me to the question of ground fault protection.
Ground fault protection is needed for a receptacle in a wet location, but has anybody had experience with how a window hvac unit and ground fault breaker agree?
It’s a $150 breaker and I don’t want to buy it to find out the breaker trips on start up. Thanks for any help or suggestions.