104F table outdoor application, free air,Besides one is for 86F and one is 104F what is the difference between the two tables? 310.15(b)(1)(1) vs 310.15(b)(1)(2)?
I have always used the 86F table. When is the 104F table used?
TIA
Always preferred equation 310.15(B), for a wider range of equipment, and conditions than idiot tables, and simple enough for a spreadsheet.have always used the 86F table. When is the 104F table used?
This is not correct.104F table outdoor application, free air,
single insulated cables
The two tables give different final ampacities, So not mix up
Correct, but my point if T310.17 used without 104F correction factor, final ampacity not same as when 104F table used directly (correction factor =1)This is not correct.
T310.17 is for "single insulated conductors in free air" and would use the 86F Table.
T310.18 is for "not more than 3 conductors in raceway or cable", and would use the 104F table.
I would think your point should be T310.17 CANNOT be used with the 104F correction factor table.Correct, but my point if T310.17 used without 104F correction factor, final ampacity not same as when 104F table used directly (correction factor =1)
Are you saying T310.17 should used base ambient temperature of 30C only?I would think your point should be T310.17 CANNOT be used with the 104F correction factor table.
Yes. 310.17 tells you it is for for conductors installed in a 30C ambient.Are you saying T310.17 should used base ambient temperature of 30C only?
So if ambient temperature 40C, T310.17 not use, even though temperature correction factors for 40C ambient temperature available in code?Yes. 310.17 tells you it is for for conductors installed in a 30C ambient.
i don't understand what you are asking.So if ambient temperature 40C, T310.17 not use, even though temperature correction factors for 40C ambient temperature available in code?
I ask why you not want apply 40C correction factor to T310.17 when ambient temperature 40Ci don't understand what you are asking.
You DO apply a correction factor for an ampacity from T310.17 when the ambient isn't 30C.I ask why you not want apply 40C correction factor to T310.17 when ambient temperature 40C
But you said:You DO apply a correction factor for an ampacity from T310.17 when the ambient isn't 30C.
Yes...that's correct. It has to be used with the 86F correction factor table.But you said:
Maybe this will help...But you said:
What it ampacity in T310.19?Maybe this will help...
#1 awg THWN has an ampacity of 195 in T310.17.
In a 40C ambient, the ampacity will be 171.6.
#1 THWN doesn't have an ampacity in T310.19.What it ampacity in T310.19?
Well, more clarity, this question:#1 THWN doesn't have an ampacity in T310.19.