Hello all,
We recently had a new 480V panel installed to serve some sensitive automotive equipment and a new 10-ton packaged HVAC unit.
Prior to HVAC unit being installed, SPD counter was at 3. Since HVAC unit was installed we have been getting an average of 4 hits/day.
There are no VFDs present and the HVAC unit is not cycling on and off frequently. We have checked for damaged wires and loose connections, even had Trane come out to investigate their unit and found nothing. That being said, when we turned off the disconnect, the surges stopped.
We are looking at moving the HVAC unit to another panel to not have it on the same source as the sensitive equipment, but have concerns the surges will still happen and the other existing 480V panels do not have any surge protective devices.
Looking for recommendations on what else to check and troubleshoot.
Thank you!
Mike
We recently had a new 480V panel installed to serve some sensitive automotive equipment and a new 10-ton packaged HVAC unit.
Prior to HVAC unit being installed, SPD counter was at 3. Since HVAC unit was installed we have been getting an average of 4 hits/day.
There are no VFDs present and the HVAC unit is not cycling on and off frequently. We have checked for damaged wires and loose connections, even had Trane come out to investigate their unit and found nothing. That being said, when we turned off the disconnect, the surges stopped.
We are looking at moving the HVAC unit to another panel to not have it on the same source as the sensitive equipment, but have concerns the surges will still happen and the other existing 480V panels do not have any surge protective devices.
Looking for recommendations on what else to check and troubleshoot.
Thank you!