journeyman0217
- Tennessee
- Electrician
I recently came across a transformer that has a high secondary output voltage. I believe the xfmr is failing. It's a 480hv - 120/208lv. Input voltage is 483. Output is 234. It does not have multiple taps and is wired correctly. As part of my troubleshooting , I used a infrared camera on it and had temperature readings of 213F on the coils and the same on the conductors coming off of the xfmr taps. I'm not quite sure what a normal operating temperature would be and I know there are multiple variables that can change the temp. The xfmr is 220C insulation and 150C rise. If the insulation is rated at 220C (428 F) then 213F on the coil doesn't seem bad. Does anyone know if the insulation rating is 220C what the max operating temp would be? 150C is 302F so the rise alone would say that 213F on the coil isn't alarming?? Has anyone taken temp readings on a normal operating xfmr? Trying to figure out what a normal temp reading is and why my secondary is so high.