Sorry folks, it was a busy few days (and I haven't read all of the replies).
Lessee...
Each side of the machine as a compressor at 19 RLA and an auger motor at 9 FLA, they auger only runs when the compressor is also running. How this works on a 50 amp breaker is left to the student, probably because nothing runs for more than a few minutes/seconds at a time. Without other checks, each side of the machine should probably have it's own 50 amp circuit but that's not how the trailer is wired.. I'm definitely going to run those down the install instructions even though we probably won't see the machine for another year. The machine is UL listed.
Operating voltage is around 210-211, connected with 50' of 6/4 SO into an outdoor distro panel and 50' of 1g(?) to the gen. No VFDs or anything fancy involved. Without a decent logger handy we couldn't catch the sag/surge.
(ETA- each side MOP 45 amp, MCA 33.3 amp)
Once we swapped in 150kva gen, that barely noticed the motors coming on and so no lights flickering - that was good enough for the weekend.
I'll post more once I've run down the machine instructions and had a few more hours of sleep, a week of 5-6 hours a night does me no favors.
Lessee...
Each side of the machine as a compressor at 19 RLA and an auger motor at 9 FLA, they auger only runs when the compressor is also running. How this works on a 50 amp breaker is left to the student, probably because nothing runs for more than a few minutes/seconds at a time. Without other checks, each side of the machine should probably have it's own 50 amp circuit but that's not how the trailer is wired.. I'm definitely going to run those down the install instructions even though we probably won't see the machine for another year. The machine is UL listed.
Operating voltage is around 210-211, connected with 50' of 6/4 SO into an outdoor distro panel and 50' of 1g(?) to the gen. No VFDs or anything fancy involved. Without a decent logger handy we couldn't catch the sag/surge.
(ETA- each side MOP 45 amp, MCA 33.3 amp)
Once we swapped in 150kva gen, that barely noticed the motors coming on and so no lights flickering - that was good enough for the weekend.
I'll post more once I've run down the machine instructions and had a few more hours of sleep, a week of 5-6 hours a night does me no favors.