Fuses
Alwayslearningelec
NJ
Estimator
Sorry for all the questions. So the 6P disconnect switch I asked about earlier makes sense as you can see the (6) #6's.
1. If I have to replace fuses in this MCC there would be SIX fuses?
2. How would I determine the size of the fuse? The disconnect switches at the units are 60A but I also see the Amps and MCA below for those same units. Assuming fuse ion MCC needs to be at least 60A?
Why are there six conductors for a single exhaust fan?
The MCA is 47.73 amps, the MaxOCPD is 60 amps so you could use a 50 or 60 amp fuse.