Open Neutral

I am not doubting you but have always wondered where that code sections is? I want to cite it next time I run into those occupancy sensors that use the equipment ground to power the electronics.
I have actually seen a range converted to run on just '240' via a 6-50 welder plug, but all the elements were 240 the guy used a 50 watt control transformer to power the electronics so nothing ran on the equipment ground.
250.140 Exception

Exception: For existing branch-circuit installations only where an
equipment grounding conductor is not present in the outlet or junction
box, the frames of electric ranges, wall-mounted ovens, counter-mounted
cooking units, clothes dryers, and outlet or junction boxes that are part
of the circuit for these appliances shall be permitted to be connected to
the grounded circuit conductor if all the following conditions are met.
(1) The supply circuit is 120/240-volt, single-phase, 3-wire; or
208Y/120-volt derived from a 3-phase, 4-wire, wye-connected
system.
(2) The grounded conductor is not smaller than 10 AWG copper or
8 AWG aluminum.
(3) The grounded conductor is insulated, or the grounded conductor
is uninsulated and part of a Type SE service-entrance cable and
the branch circuit originates at the service equipment.
(4) Grounding contacts of receptacles furnished as part of the equipment
are bonded to the equipment.
 
I wonder if the neutral current on the grounded conductor is higher or lower on a modern electronic range. The old ones were timer, light/lights, and those single receptacles that I never use. Maybe the oven lock solenoid on the self cleaning ones
 