Alwayslearningelec
- NJ
- Estimator
What is the size of a motor disconnect switch based off of? How would one calculate? Is it the breaker size feeding it?
Not necessarily. As mentioned 115% is the general rule. Inverse time breakers can be 250% of FLA to allow motor starting.Is it the breaker size feeding it
No, I have never seen that.Has anyone ever seen a disconnect switch with a HP rating that was actually less than the 115% that Augie mentioned?
Isn't there a top end for HP switches? I haven't looked but in my mind bolted pressure switches didn't have HP ratings nor did MV switches.Has anyone ever seen a disconnect switch with a HP rating that was actually less than the 115% that Augie mentioned?
I am used to looking at the voltage and HP rating of the disconnect . 430.110 gives more info.What is the size of a motor disconnect switch based off of? How would one calculate? Is it the breaker size feeding it?
I asked because I seem to remember a scenario in the field years ago where the HP rating of the switch was less than the 115%. If I had to guess the numbers were very close as far as being just under the 115%.Which begs the question as to why the NEC allows it in the exception to 430.110(A)! I imagine that at one point in the past, someone must have made a "HP rated switch" that did not meet the 115% rule, i.e. it was rated somewhere between 100% and 115% of the specific motor FLC.
Yes, I remember a similar situation. IIRC, it was a 30 Amp disconnect. I had to move up to a 60. IDR if it was 1 or 3 phase.I asked because I seem to remember a scenario in the field years ago where the HP rating of the switch was less than the 115%. If I had to guess the numbers were very close as far as being just under the 115%.
I run into where fused switch needs to be next frame size because of the fuses necessary to hold during motor starting, where otherwise unfused switch from same product line can be the lower amp rated switch. Example 20 HP @ 480 volt three phase can use 30 amp Square D unfused disconnect as it is rated 20HP at that voltage but if you need fused switch you have to go to the 60 amp switch as you will need 45 or 50 amp fuses if it is started across the line. Their 30 amp fused switch has the same switch but the 30 amp max fuse is a limiting factor and those are only marked 15 HP @ 480 volts.Yes, I remember a similar situation. IIRC, it was a 30 Amp disconnect. I had to move up to a 60. IDR if it was 1 or 3 phase.
Don't forget that non-fused disconnects are only rated for 10 kAIC, but fused disconnects can get you to 100 kAIC or more. If you have high available fault current, you might need to go with a fused disconnect and maybe a larger size as kwired says.I run into where fused switch needs to be next frame size because of the fuses necessary to hold during motor starting, where otherwise unfused switch from same product line can be the lower amp rated switch...
Yes, good point.Don't forget that non-fused disconnects are only rated for 10 kAIC, but fused disconnects can get you to 100 kAIC or more. If you have high available fault current, you might need to go with a fused disconnect and maybe a larger size as kwired says.