Roofing screws through conduits, how to test live circuit insulation?
CurSol1!
New User
Boston
Electrician Master
Here's a good head scratcher for you guys and gals.....
I've been in the trade for over 40-yrs now and yet I cannot figure out how you can test to see if a live conductor that is nicked by a screw in a conduit and could be leaking to ground but yet not bad enough to trip a breaker.
One of our customers had a very large rubber roof (50,00SF) where the roofer has penetrated many conduits with their 6" rubber roofing screws.
My guys found a few in just the first look. We usually provide insulation resistance test reports using our meggars but always on de-energized circuits.
When this building was originally built, our code did not address conduits above bar joists and in the corrugated metal pan roofing and of course in this case, there could be upwards of at least thousands of screws, 50 or more conduit runs with hundreds of live circuits.
To make matters worse, we do not have as-builts to help us determine where all the branch circuits go and what are connected to them, so now that just by pulling the conductor off the breaker and inducing upwards of 1000V into the conductor with our meggar is going to result in countless printers, computer, tv's damage and who knows what..... so with that said:
Is there any way to test a live conductor's insulation resistance value (leakage to conduit/ground) with unknown loads on that conductor's circuit?
Playing the devil's advocate and hoping for some valued input:
If we turn off the breaker, could we read the resistance value from conductor to conduit? Whatever is plugged into that circuit is probably going to provide bad readings though, correct?
Do you think that if we data log amperage we may find some anomalies? Motor start or any load turned on is going to blow that theory.
Talk about a needle in a haystack, I told our customer to initiate an insurance claim against roofing company because a dead short could happen now or it can happen in a year if you have a nicked wire and the roof heats up or the insulation breaks down over time, you'll then get that fault. I feel bad for our customer, but we are at a stand-still as to how we can attack and dig into this one...
Norman
Short of megging all of the circuits (which would be difficult without removing all loads) one possibility, though not fool proof, would be measuring current on the SBJ. Turning off feeds watching for current drop. Then divide and conquer until the offending circuits are found. A caveat though, it could be a leakage from a faulty piece of equipment too.
Norman
Use leakage current clamp meter putting both conductors through the meter detect ground fault current on damaged insulation. Individual circuits below roof may also check , locate damaged portion
Yes, it would be worth doing this with a leakage current clamp meter capable of reading ~1mA and preferably less.
You could first put the clamp around all of the wires in a conduit. Then see what kind of variation in the leakage currents between conduits you are seeing. Starting with the conduits having the highest leakage, identify individual 2-wire and MWBCs and measure each of their their leakage cuurents. As @hillbilly1 mentioned, some equipment could be contributing leakage current and may need to be identified before blaming the leakage on the wiring.
EGC to spare, it reduce actual leakage current
Better, off such equipment or all equipment with power in conduits
Having the load drawing current will help identify any screw penetration to the neutral, due to its causing the diversion of some of the load current.
And so having the load turned ON, OFF, and even totally disconnected could provide additional information as the testing proceeds.
Talk about a needle in a haystack, I told our customer to initiate an insurance claim against the roofers and roofing company because a dead short could happen now or it can happen in a year if you have a nicked wire and the roof heats up or the insulation breaks down over time, you'll then get that fault. I feel bad for our customer, but we are at a standstill as to how we can attack and dig into this one...
Norman
You can’t properly test insulation resistance on a live conductor because insulation resistance testing must be done with the power off. If a live wire has been nicked by a screw and is leaking to ground but not enough to trip a breaker, the safest way to check while it’s energized is to use a leakage current clamp meter around the conductors. This can show any imbalance between the current going out and coming back, which would indicate current leaking to ground. You can also compare the hot and neutral currents with a true RMS clamp meter; if they don’t match, there’s leakage. Beyond that, the only accurate method is to de-energize and isolate the circuits, then perform insulation resistance testing safely.
I think this is the best suggestion for generating the short list of circuits for which one then needs to disconnect load and properly megger.
What a s---show, I hope an insurance company comes through.
If the screw nicked the wires there would be arcing? Is there a way for an oscilloscope to detect arcing in a circuit? Or maybe a infrared camera may see the arcing hotspots? ( I guess you would need to be rather close to see the hotspots)
Home Depot has a lot of old stores that were done that way. I was tasked with finding a way to locate and mark the roof where the pipes were run economically, but never did before I was onto another task. I know there’s got to be a way to maybe detect the electrical field, but with the metal decking, and metal conduit, I think the field would be hard to detect without interference from the light fixtures.
i would be less worried about a 'leakage' to ground, and more worried about damage to the conductor itself. how many breakers did you have trip, while these roofers were running screws, through your conduits? every one of them, should be chased down, and repaired on the insurance company's claim, if that's the route you're going.
we know that the cross-section of the conductor is what gives it it's ability to pass amperes without excess heat and causing damage to its insulation and the other conductors next to it in the same conduit. therefore, we must realize that taking a chunk of copper out of a conductor will severely cut down the ampacity of that conductor, at the point of the knick. each one of those screws that tripped a breaker, had enough of a fault to damage the conductor itself. even if it somehow blew itself clear, and is now holding ok. that spot could get much hotter than the rest of the conductor, at a later date, and cause issues with everything else in that conduit. and, trying to go back in a year or two after that conductor finally fails in the pipe to make a claim, is probably not going to work out very well for you or your company.
IMO - if it had a breaker trip, each potential de-rating knick of conductors inside of a conduit needs it's damage repaired NOW, before it turns into an emergency situation, where you're stuck being there overnight or on the weekend, trying to get the equipment back up and running.
my second question would be, are the damaged conduits at least the 1.5" below the roofing steel, as required by NEC code? if not, you may be denied insurance claims, and simply stuck with fixing things yourself, unless you can prove they were installed before 300.4(E) was written into the code. i don't have all of my old copies of NEC here at home, but the internet is saying that went into effect during the 2008 NEC code cycle.
i wish you good luck on this situation. it sounds like you have a lot of work ahead.
Seems like a live one would have been evident? A screw thru a steel pipe should be about as good a ground as it gets.
Exactly. There is no way to know where a screw penetrated a conduit and shorted out the conductors until it actually happens. Unless you can actually see the damage, any effort at this point is a waste of time.
The liability rests squarely on the roofer. They and the building owner need to get the insurance companies involved ASAP and have them determine what they will do about hidden damages that show up years down the road.
My suggestion would be to rip it all out and replace it at the roofer's cost.
-Hal
Insurance is going to say "show me what is shorted" and you can't so they will say its not shorted now. I don't know when the change was made about not running the pipe above the bar joists but everything was run that way around here before the change. When did it change 20 years ago?
Why do they run such long screws anyhow although if you against the deck it doesn't matter.
It’s so they can hit the lower or higher part of the decking.