failed inspection cat6 cable not to code
Haven't heard of Monk, but that number looks a lot more realistic (FWIW, I think we pay something a little over that for Commscope's cable, and I don't even want to guess at how much we go through in a single year).
I researched quite a while trying to find a decent brand for the money with a heavier gauge, solid copper conductor. It does what I needed it to. Pulls out of the box good too.
Thanks everyone what a bummer, I completely missed the copper clad aluminum part. Also apparently some of the ceiling space might be a plenum, but I think some of the HVAC was redone some years back so patient care does not use a common plenum.
either way it looks like this cable is going in the dumpster.
The IT people throw around so many fancy terms I have no idea what they are talking about so I figure they know to get the correct cable turns out no they don't have a clue about the cable.
It had some printing on it but not CMR or CMP, the IT guy supplied it, I should have known better than to just install it, thats the problem with customers providing materials and being in a rush these days.
Are there any other special requirements for data cable in a medical clinic?
Thanks everyone lesson learned.
Critically, what code sections did the inspector give you on the violation report? We really can't be helpful without that information. Everything else is wild speculation.
The only issue I see is whether the cat 6 is CMP or CMR rated. Preferably solid core cat6 but CCA is acceptable, imo. Although I've never run into a jobsite with CCA cable or ever installed CCA. I would get the reason "why" from the inspector as to it not being acceptable? To answer your question, There are NO "Special Requirements" for cat6. Hope this helps! For name brand cables, Belden, Commscope or Tyco/TE are great.
Commscope is what our physical networking guys use at the office, while my typical source for RS485 wire is WestPenn. I was teasing Hal earlier about how much Belden costs versus the others, but if you need something arcane, they're pretty much guaranteed to have it.
Its NOT acceptable. The design standard for CATx cable is to be manufactured with copper conductors. Any cable made from other that copper is not a CATx cable.
None of the jacks or plugs are designed for CCA. Using CCA for PoE may not work and could be a fire hazard. As Don pointed out in post 5, its a violation of 725-144 to use CCA for PoE.
I don't believe any of the CCA cables are listed even if the claim to be. Any info such as type of jacket may not be accurate since there is no third party testing.
Roger that! Thank you for the update. I did not know that, now I do.
Yeah thanks again all we just replaced the cable with plenum rated copper so I would not need to diagram the HVAC and hold up the CO any longer.
The inspector eventually got back to me said to start with it was a violation of sections 800.179 and 725.144.
Table 725.144 is one I had not seen before. That seems to put a current limit on cables that are bundled. Network cable bundles can be huge. Hopefully your new cable will be 75C rated and POE needs limited. I can see this being hard to enforce if non-POE switches get replaced with POE switches and more and more POE items get added to the network.
The way it was explained to me is the inspector has make the most conservative interpretation unless things are clearly marked and identified otherwise like different colored cables or I don't even know.
All the inspector knows is unless there is 0% chance power can be flowing you have to treat it as if there is.
The problem is the Copper Clad Aluminum (CCA) cable. This is a major code violation.
The National Electrical Code (NEC) requires communications cables (like Cat6) in most commercial installations to be CMR (Riser) or CMP (Plenum) rated. CCA cable does not meet these safety ratings.
Why it Failed:
  1. Fire Safety: CCA cable has different burning characteristics than pure copper and is not listed by a recognized testing laboratory (like UL) for use in walls.
  2. Performance & Reliability: CCA is inferior for data. It's more brittle and has higher resistance, which can cause network failures and power over ethernet (PoE) issues.
Solution: All that CCA cable must be removed and replaced with certified pure copper (Bare Copper) Cat6 with the correct CMR (for riser spaces) or CMP (for plenum air spaces) rating. Never let a client supply cable unless you can verify its specifications first.
Nothing in article 800 likely applies to your situation. Only applies to what it says it applies to. Read carefully that paragraph.
Why would it not apply? It sounds like he installed an ethernet system's cabling. That sounds like communications circuits for communications systems. I can see article 725 applying too.
I know of no reason why you can't use CM listed cable in commercial as long as it isn't an environmental air space or a riser. If all the wiring stays on a single floor, CM is probably fine. It is probably easy to hit an air space above a dropped ceiling and maybe a riser in a multi floor building, so CMP is always a safe choice.
Commscope is what big Orange uses for their networks. Commscope also has “Redwood” which is lighting using POE. (I assume they still have it, it’s been years since I’ve been through Commscope training)
For fire alarm, my company doesn't use anything other than FPLP, which is a type of CMP. Unless you are putting in literal miles of cable, the labor cost of fixing a mistake will wipe out any savings in material. In fact, I just checked the pricing for 16-2 unshielded for a 1,000-foot box at ADI, and they're all between about $180 to $190, riser or plenum.