Dsg319
Senior Member
- Location
- West Virginia
- Occupation
- Wv Master “lectrician”
I took it as 3phase source with a single phase load.Said 3 PHASE, yet no C phase load in that at all. Are we to just guess?
I took it as 3phase source with a single phase load.Said 3 PHASE, yet no C phase load in that at all. Are we to just guess?
That's exactly what the question was about. Feeding single phase loads from a 120/208 panelboard is commonplace in commercial applications. People should not be having a hard time with this question.I took it as 3phase source with a single phase load.
No, just answer the question as asked. Guessing on information or adding information is a fatal mistake for passing exams.Said 3 PHASE, yet no C phase load in that at all. Are we to just guess?
Maybe completing the info would be better. OP should have said three phase with single phase load.No, just answer the question as asked. Guessing on information or adding information is a fatal mistake for passing exams.
Maybe the question was written the way he posted it. For an NEC reason for the question 310.15(B)(5)(b) would cover it.Maybe completing the info would be better. OP should have said three phase with single phase load.
Perfectly valid question because many would guess that the correct answer is 10-5=5 amps which is wrong. He said A=10 amps, B=5 amps, 208 volts, 3Ø system. That question is answerable without guessing.Said 3 PHASE, yet no C phase load in that at all. Are we to just guess?
He said three phase, not three phase system. There is a difference.Perfectly valid question because many would guess that the correct answer is 10-5=5 amps which is wrong. He said A=10 amps, B=5 amps, 208 volts, 3Ø system. That question is answerable without guessing.
How so? He stated 3 phase, 208 volts with a neutral what other system could it be besides a 208Y/120?He said three phase, not three phase system. There is a difference.
He said three phase, not three phase system. There is a difference.
That's exactly what was asked by the question. If this were a test question it would be designed to trick you by only including the minimum amount of information to find the answer. No need to read anything else into it.I thought 3 phase with only a single phase load but what do I know?
There was no mention this was a test question. Then there is no mention of I of C, so you are not left to "guess", but rather make assumptions, and that's where things can get sideways. Would it really be excessive in a test question to simply say either C is not connected or 0A?Perfectly valid question because many would guess that the correct answer is 10-5=5 amps which is wrong. He said A=10 amps, B=5 amps, 208 volts, 3Ø system. That question is answerable without guessing.
Yes it would be if the purpose was to show that you actually understand that in a 3Ø, 208Y/120 volt system that when only the A and B phase values are given the neutral current is not found by simply subtracting 5 amps from 10 amps. The correct answer can easily be found with the information given which is the point of the question.Would it really be excessive in a test question to simply say either C is not connected or 0A?
Agree to disagree. I live in the real world. The information in the poorly worded question indicates THREE PHASES! I want to know what all three are doing! I mean sure, select the most practical answer on a test and move on, but in the real world, this doesn't really hold water.Yes it would be if the purpose was to show that you actually understand that in a 3Ø, 208Y/120 volt system that when only the A and B phase values are given the neutral current is not found by simply subtracting 5 amps from 10 amps. The correct answer can easily be found with the information given which is the point of the question.
I agree we can disagree. If this were a 3-wire MWBC there would be no C phase current because there is no connection to the C phase. Someone reading the question should be able to understand that is what it says given all of the information provided. If they're unfamiliar with 208Y/120 systems then they probably won't understand the question and say that the neutral current is 5 amps.Agree to disagree. I live in the real world. The information in the poorly worded question indicates THREE PHASES! I want to know what all three are doing! I mean sure, select the most practical answer on a test and move on, but in the real world, this doesn't really hold water.
I didn't see anything of the like. 208 3P with a neutral. Got it, a 208/120 4 wire panel. Apparently clamp meter only fits on 2 of the wires...lol But anyway, the point of the question, IF it's even a test question at all, is understanding the 120* phase relationship with neutral, as opposed to 180* in a single phase/split phase arrangement. It would not matter how you arrive at the currents on A and B. It just doesn't. All that matters is those 2 phases are 120* apart with respect to their neutral for the purposes of calculating the neutral current.So it seems it boils down to how each of us perceived the question. Some saw it as a 4 wire wye MWBC missing information, others saw it as a 3 wire wye MWBC. In either case the 3 wire version can be solved as is and for those who want it to be 4 wire just add a number for the missing value and solve it.
Bingo.All that matters is those 2 phases are 120* apart with respect to their neutral for the purposes of calculating the neutral current.