lynchmatt23
- Philadelphia, PA
- General Contractor
Reaching out regarding a common issue I run into when completing short circuit studies. For reference we are an electrical equipment supplier for commercial projects and our scope typically includes the power system study consisting of coordination / short circuit and arc flash analysis. Study is completed by 3rd party PE. On projects where there are electric water heaters (domestic water not HVAC) it seems that they always fail the short circuit analysis. I have yet to see a manufacturer indicate a short circuit current rating on their documents for these units and therefore the study engineer just assumes 5 kA. The manufacturers always say that the UL listing (either UL 174 or UL 1453) does not require units to be labeled with a short circuit current rating. I understand that there are many instances in the NEC where they call out requirements for SCCRs on particular types of equipment but I have yet to see a section requiring this for domestic water heaters (electric or otherwise). However, these heaters have control panels with terminal blocks / relays / fuses / etc. so there must be an overall rating for the controller. The discussions I have had with engineers of record on these projects are typically met with blank stares and I haven't come up with a real answer on the situation. At this point I think this is just a grey area in the code and at some point there will be an update to capture the SCCR requirements.
Has anyone else ran into this or have feedback on this issue? See links below for examples of units.
www.rheem.com
www.eemax.com
product - Rheem Manufacturing Company
www.rheem.com
FlowCo | Eemax
www.eemax.com