Something else you may want to look into for a fire system cooking line equipment shutdown.
In my area, the fire marshals require that the hood air make up unit, for the hood supply, shuts down with a fire system trip. At the same fire control head trip time, it is required for the hood exhaust fan to remain running or automatically turn on if it is off when the fire system trips. They also require a fuel gas solenoid shutoff if there is any gas fired equipment under the hood.
if that is the case in your area, you don't want to supply the exhaust fan from the panel that you are going to put the shunt trip breaker on.
The fire suppression installer/contractor also supplies a reset relay that prevents turning on any equipment or circuits until the fire system head is reset and the reset button on the relay is pushed to enable the electrical system reset.
The purpose of the air makeup shutdown and the automatic exhaust fan run is to help avoiding feeding air to a fire and pushing it away from the hood and equipment, while drawing the fire into the solid welded exhaust stack. to help prevent the fire from spreading out into the building. Check with the fire contractor installing the job and the fire Marshall to be sure before you start.