Short Circuit Current
Zyb
Maine
Design Engineer
Do I need a fusible switch, if a typical non fusible is only 10kAIC. 39kA and 18kA are available fault currents?
Check with the manufacturer.
Most, if not all, nonfusible switches have 100kA series ratings with upstream fuses.
Many also have series ratings with upstream breakers from the same manufacturer.
  • Like
Reactions: Zyb
@Jraef, so if i use 100kAIC fuse on my first switch then rating on my NF switch will be 100kAIC? just want to make sure i got it right. Thank you!
FWIW: I find it hard to believe that the fuse would protect the switch on its line side, but not the switch on its load side.
I don't know what you are getting at.
SCCR is always dpecified as being at the incoming/line side terminals of a device.
No issue, if a manufacturer not listed such combination, a PE can certify the combination
No, they cannot.
The NEC makes no provisions for field engineered SCCR series ratings of non-fused switches.
The only NEC allowed engineered series ratings are for circuit breakers without instantaneous trip functions.
But op asking to replace with 100kA fuse in fusible switch marked with 39kA!
There is no fusible switch rated at only 39kAIC.
The OP needs a 39kA minimum fused switch to protect a non-fused switch which has 18kA available. The manufacturer literature says an upstream fuse can series protect a downstream switch up to 100kA, so the OP's installation meets the NEC, as long as fuse rejection clips (disallowing 10kA fuses) are installed in the upstream switch.