MC Cable Out Of Panel
Alwayslearningelec
NJ
Estimator
Trying to propose allowing MC cable out of panel in lieu of EMT in some cases. What's the disadvantage of using MC out of a panel? Can pull any additional wires as you might be able to do with EMT is the only think I can think of.
Also, how often do you see same circuits from different panels( say normal lighting and power) in same conduit if same voltage?
You can come directly out of the panel with MC cable unless subject to physical damage. It's a design issue. Some places might require EMT if in an electric closet.
In my opinion it is exclusively a cosmetic issue. Well run conduit looks good. Well run MC looks between OK and a little messy.
You could pull additional wires with FMC....
Where physical damage is a concern at lower heights in an electrical room I've seen EMT run out of the top of the panel for 3-4' and then switched over to MC using an EMT to MC transition fitting.
I've seen few time this transition, in this case the mc cable terminate in the fitting and the conductors run in the emt?the insulation of conductor in mc cables are not thhn, any concern on this? some limitation in this type of run beside the imposibility to add more circuits in the conduit?
I personally never used this transition and prefer run the mc cable from panel all way to first box or use emt with regular thhn insulation conductor.
I think it’s more for aesthetics and ability to add circuits. Residential has that problem when all of the knockouts are used up due to the number of cables. Hotels seldom add circuits after they are built, so not such a big deal there.
It's all about "impact zone". Can the cable be impacted by something crushing it? In my area MC is discouraged below 8'. It just depends, like if the panel is in a closet the chances of impact are low. In a garage, the chances are high.
What’s the building material that eats mc cables armor?
Is it cinder block that eats aluminum?
I heard somebody run exposed mc cable to a panel and years later there were only bare conductors.
I've been doing this for 20 years and very rarely have I had a problem running MC directly in to a panel. Its also about money. Using pipe can be more money and time. There are times when it has to be protected but even then you can sometimes just build a wall around the cable.