newbee_one
 - Ohio
 - retired
wwhitney replied to the above thread on April 17, 2024 (framed around finding the appropriate conductor size for a 25A continuous load across 8 conductors in a conduit):
Putting those two together for a 25A continuous load, 75C termination temperature, and 90C insulation temperature, then 210.19(A)(1) (and the similar sections for feeders and SECs) says that you need a conductor whose 75C column entry is at least 31.25A, and whose 90C column entry is at least 35.7A.
However, for a continuous 25A load, you also need a 35A OCPD. So 240.4 also requires that you have a final ampacity of at least 30.5A so you can apply 240.4(B). That means that you also need a conductor whose 90C column entry is at least 30.5 / 0.7 = 43.6A. This requirement is stricter than 210.19(A)(1)(b), so the final answer is a conductor whose 75C column entry is at least 31.25A, and whose 90C column entry is at least 43.6A.
This procedure never requires doing the computation 25A * 125% / 0.7 = 44.6A. That figure is irrelevant.
Cheers, Wayne
Regarding the (in the blue text area above):
First sentence: Where did the 35A OCPD come from? Is it simply the upgrade of the minimum 240.4(b) amperage (30.5) to the next standard rating?
Second sentence: I interpreted the use of 30.5A as the minimum load needed before 240.4(b) could be used (assumedly to avoid the use 240.4(d) small conductors clause).
Third sentence: I'm curious how the 30.5 / 0.7 = 43.6 calculation would change if the continuous load was 35A not 25A. Would the 240.4(b) calculation then be 35 / 0.7 = 50A? Giving a conductor whose 75C column entry is at least (35 * 1.25 = 43.75A), and whose 90C column entry is at least 50A.
thanks in advance for any help.
			You basically have it correct, but let me elaborate on your answers:You have me confused also.
If you have a 25A continuous load, then 210.19(A)(1)(a) (and the similar sections for feeders and SECs) says that at the terminations you need an unadjusted and uncorrected ampacity of at least 31.25A. That would be using the table column for the termination temperature, typically 75C, occasionally 60C.a.) I have a 25 amp load that would be 31.25 after the 125% for continuous load was added.
If you have a 25A load, continuous or non-continuous, doesn't matter, then 210.19(A)(1)(b) (and the similar sections for feeders and SECs) says that you need a conductor with a final ampacity of 25A. With a 0.7 adjustment factor and no temperature correction, that means you can use the table column for the conductor insulation temperature, typically the 90C column, and look for a conductor that is at least 35.7A in that column.b.) I have the same 25 amp load but I have an adjustment factor of 70% because of number of conductors in a conduit. 25/.7 = 35.7 amps
This means I need a conductor good for 35.7 amps
Cheers, Wayne