MyCleveland
- Cleveland, Ohio
Let me first say...In EasyPower, the ONLY impact of setting a different ambient temperature is determining the ampacity of the conductors. The program will derate the ampacity based on the NEC derating requirements. That's it. There's a different parameter for adjusting the actual conductor temperature.
Regarding the "as-delivered" default of 50 deg C for the conductor temp - the "worst case" conductor temperature depends on the study being performed. For short-circuit calcs, a lower temperature would give higher fault currents. For power flow, a higher temperature would give a higher voltage drop and power loss. Again, we're talking about small changes in the results.
One of the features I like about SKM is that you can specify two different conductor temperatures - one for short circuit and one for power flow. You could do that in EasyPower using Scenarios, it would take more work.
IMO, we're taking the NEC conductor data resistance table too seriously. It is strictly informational, AFAIK. Any conductor resistance table has to be based at a specific conductor temperature - they use 75 deg C. But nowhere does it say that you should use 75 deg C for your short circuit calculations or voltage drop calcs.
JD
I am not ignoring you, I just simply cannot formulate a response. I always read your comments and appreciate the time you spend.
DC
I just ran a single test calc of 200' of THHN CU using the NEC table values at 30C & 40C.
2% difference seems important.
8% difference if I drop the loading to 100A vs the fully loaded NEC 75C value.
My understanding from actual users (6 years ago) was that the values where verbatim from the NEC tables for BOTH EP & SKM.
I could not agree more, but believe the majority is without adjustment for either calc type.
We can leave it here, no one else has interest in the topic.
I thank you both for your time.