Service feed overcurrent protection for multi-unit EV charging
Not sure if the poco would turn over each individual's power history to a condo board, so may need to have each owner give permission to give it out. If the poco doesn't have this data, then it isn't a solution, but you could possibly put some power recording device on the service to measure it.
The original funding premise for smart meters included a local area network. This actually appeared to various degrees.
But some utilities do it, including in my areas:
  1. Astech IHD
  2. EcoBee Si
  3. Embertec Emberpulse
  4. Rainforest Eagle Gateway
  5. Universal Devices ISY994 ZS
  6. LG EnerBox2
  7. Emporia Vue: Utility Connect
But that said you'd want a local connection, not a fragile cloud connection.
But for those answering, note this is a DIY request by a new member not in the electrical trade.
Im curious what info is available over wifi from the meter. I have a Rainforest device connected to my meter via wifi that shows current usage and it updates about every 30 seconds. So obviously that is there. Wonder if the 15 minute interval data is available and does it store it. If so, how much is stored before you have to read it because it gets overwritten?
Do you have smart meters on the building and does the utility keep 15 minute interval usage data per meter? If so, and you can get that for all units, all you need to do is sum the loads of each unit together if they use the same time intervals (assuming the car charges are coming off of each units panelboard) and check the total KW being drawn. This is like what you do in 220.87 to do a load calc based on usage instead of overly conservative calculations.
Not sure if the poco would turn over each individual's power history to a condo board, so may need to have each owner give permission to give it out. If the poco doesn't have this data, then it isn't a solution, but you could possibly put some power recording device on the service to measure it. Someone needs to read the data monthly or quarterly to see what the loads are. Continuous loads are a bit tougher to measure as 220.87 data asks for 15 minute intervals. You would need to find the worst case 12 consecutive intervals to get a continuous number. Probably doable with an Excel file, and my poco provides the data in excel format directly.
I also wonder about your assumptions in post 1. A 90A breaker to a unit doesn't mean their load calc is 90 amps. How did you determine it was a 600A service? Did you see multiple 200A breakers in meter stacks and add them up, or is there a single 600A main, or did you examine the service conductor size to see what it is. If there are multiple service disconnects, they are allowed to sum to larger than the calculated service and most likely are. The service conductor must be sized to the calculated load, not the sum of the main breakers when there is more than one.
Why not op automate the process with his less than $1k constraint using smart energy monitors?
I was going to say something similar. Rather than all this rube goldberg stuff that is probably way overly conservative anyway, put a logger on it (if poco data not available). You can get a set up from EKM metering for like $500.
Maybe you could get 2 setups, one could just live on the service, and another one could be moved around to tenants as they want chargers (presumably not everyone wants one right now?)
Does the primary transformer to the building have enough capacity for this? That's where I would check first to see if this is possible.
Why? That's almost certainly the utility's problem, if it is one.
They get upset when there's a lot of load nobody told them about.
But this is just because they don't monitor those transformers well.
And, wickedly undersize conductors.
The picture is a new 400A service with a new drop.
Note the relative size of the NEC conductors vs. the POCO conductors.
POCOs get away with "free air" wire scheduling. I've got the same issue in a building in downtown KCMO. #2 AL feeding two buildings and my new 200A service. ??
They also may have 90C rated terminations. My last house was like that photo -- 400 KCMil copper up the mast, 1/0 aluminum service drop from the utility. They were going to leave the 25 KVA transformer too, but I paid extra to bump it to 50. After running stuff for a while, a 37.5 KVA probably would have been enough.
I arrange EV loads to be non-coincident. Does that change your thinking ?
Not really. When people get home from work around 6 pm they all plug in for the next day. EV ranges are overstated from the manufacturer, among other issues. People want level 2 charging at home, and now they want level 3 with cyber trucks which I think are totally stupid.
Published EV range is based on EPA tests, just like MPG for ICE vehicles.
That's not the issue we were talking about. The issue is the you shouldn't "derate" EVs like an apartment complex with electric dryers. I would assume that all EVs are plugged in at once. It's entirely possible.
my point was that people are disappointed with actual EV ranges and are freaked out not having enough charge to get through the next day and plug in whenever possible all the time.