SureFire
Member
- Location
- Wake county, NC
- Occupation
- retired IT Systems Engineer
Background:
Single family detached residence built in 1977. Electric range is wired as explained in the exception stated in 250.140. i.e. There is no EGC in the dedicated branch circuit for the range. Therefore, the frame of the range is bonded to the grounded conductor. Circuit breaker is 2-pole, non-GFCI, 50A. Let’s call this circuit A.
There is another branch circuit very near the range whose conductors, hot, neutral, and ground, are 10AWG copper. Let’s call this circuit B. Per Table 250.122, a 10 AWG copper conductor can be used as the EGC in a branch circuit up to and including 60A.
Both branch circuits originate from the same load center. The load center and the range are on opposite ends of the house. No easy crawl space, basement or attic access.
p.s. Because of extensive damage from hurricanes, our state is still using NEC 2017.
Question:
Can 250.130(C)(4) be used to do the following?
Single family detached residence built in 1977. Electric range is wired as explained in the exception stated in 250.140. i.e. There is no EGC in the dedicated branch circuit for the range. Therefore, the frame of the range is bonded to the grounded conductor. Circuit breaker is 2-pole, non-GFCI, 50A. Let’s call this circuit A.
There is another branch circuit very near the range whose conductors, hot, neutral, and ground, are 10AWG copper. Let’s call this circuit B. Per Table 250.122, a 10 AWG copper conductor can be used as the EGC in a branch circuit up to and including 60A.
Both branch circuits originate from the same load center. The load center and the range are on opposite ends of the house. No easy crawl space, basement or attic access.
p.s. Because of extensive damage from hurricanes, our state is still using NEC 2017.
Question:
Can 250.130(C)(4) be used to do the following?
- Replace the NEMA 10-50 receptacle with a NEMA 14-50 receptacle.
- There will be two cables going into the NEMA 14-50 receptacle. The original 3 wire, 4 AWG aluminum cable. And a new 10-2 with ground copper cable. The hot and neutral conductors of the 10-2 will be capped off and not used. The 10-2’s EGC will be connected to the ground terminal screw of the NEMA 14-50 receptacle.
- The other end of the 10-2 cable will be joined to circuit B inside an existing J box. The hot and neutral conductors will be capped off and not used. The EGC will be connected to the EGC of circuit B.
- Inside the J box, label the new 10-2 as ‘Kitchen range EGC only’
- Replace the range’s power cord with a NEMA 14-50 power cord.
- Unbond the ground and neutral in the range.
- Replace the 50A breaker with a 50A GFCI breaker.
- In the circuit directory (the documentation showing what each breaker protects) for the load center, make a note that the EGC for the kitchen range is connected to circuit B.