is this graphic correct?
or should 3' vertical line extend to the floor?
2020 nec
(C) Bathtub and Shower Space. Receptacles shall not be
installed within a zone measured 900 mm (3 ft) horizontally
and 2.5 m (8 ft) vertically from the top of the bathtub rim or
shower stall threshold. The identified zone is all-encompassing
and shall include the space directly over tl1e tub or shower stall.
Exception: In bathrooms with less than the required zone the recepta-
cle(s) shall be permitted to be installed opposite the bathtub rim or
shower stall threshold on the Jarthest wall within the room.