Frank D
Member
- Location
- Los Angeles, CA
- Occupation
- Electrical project manager
We have a client with current on the GEC. The facility has 2 480V 3 phase 3,000A services, each fed by a separate utility transformer.
Service 1 has a current (it varies + or - 10%) present on the GEC of 4.5 amps.
Service 2 has a current (it varies + or - 10%) on the GEC of 25 amps.
The site is a resort, with service 1 providing most of the mechanical equipment, and service 2 providing most of the 120 volt loads, the hotel rooms and some small mechanical equipment.
Understanding that the GEC should not have constant current present, and that there has been only minimal work done since the original construction, I haven’t found any evidence of a design flaw, and have not found the culprit.
The interesting part, is that the current is respective to the proportion of the single pole loads. The majority of the 1 pole loads are on service 2, with the highest ground current.
Comments welcome.
Service 1 has a current (it varies + or - 10%) present on the GEC of 4.5 amps.
Service 2 has a current (it varies + or - 10%) on the GEC of 25 amps.
The site is a resort, with service 1 providing most of the mechanical equipment, and service 2 providing most of the 120 volt loads, the hotel rooms and some small mechanical equipment.
Understanding that the GEC should not have constant current present, and that there has been only minimal work done since the original construction, I haven’t found any evidence of a design flaw, and have not found the culprit.
The interesting part, is that the current is respective to the proportion of the single pole loads. The majority of the 1 pole loads are on service 2, with the highest ground current.
Comments welcome.