Alwayslearningelec
- NJ
- Estimator
So are you saying you can't use flex as EGC and thus the jumper?NYC codes do not consider flex connectors as qualified grounding bond. I have seen new MC connectors that bond like this. It's kind of insane if you ask me.
NYC Article 250 is no different than the NEC with a few minor exceptions. These bonding jumpers aren't one of them. Can you cite something specific?NYC codes do not consider flex connectors as qualified grounding bond. I have seen new MC connectors that bond like this. It's kind of insane if you ask me.
So you think they unnecessarily installed them or did because it was in spec?NYC Article 250 is no different than the NEC with a few minor exceptions. These bonding jumpers aren't one of them. Can you cite something specific?
As infinity pointed out, if the conduit/flex doesn't contain an EGC (or SSBJ) then the bond would be needed but it would need to be installed correctly. If the conduit/flex has a wire type EGC then the is not necessary according to the NEC. but might be required by spec.So you think they unnecessarily installed them or did because it was in spec?
I doubt that the screw that is holding the connector together has been evaluated to carry the fault current associated with a bonding jumper that size. If there is an EGC within the raceway then no jumper is required around the flex.So you think they unnecessarily installed them or did because it was in spec?
Take a look at 250.118 for when FMC qualifies as an EGC and when it does not. If flexibility for vibration mitigation is required for something like a transformer then the FMC does not qualify as an EGC.So conduit service as an EGC correct? The flex would not qualify as one of no wire type one is installed within conduit?